So can I add 400a
fuse to multi
inverter / charger at start of wire inside cover then plug straight to
battery bus bar ? As im using Anderson plugs. 35mm, for now but not constantly. but I'm looking for 70mm wire connection's if out there. 2023 jan.
And can I plug and play or do I need the head set or rasp pi ? as im into plug and play by dip switches. If they are set out of box for 12
It will work out of the box, but will be set to 16A input, I think.
That's not going to be a problem, until you are on hookup and turn on more than 13A of stuff. (And that includes the amount the charger is taking)
Edit: Fuses need to be wherever is the source of the power. So, next to the
battery. No
fuse is needed inside the
multiplus as it can only supply 16A, your cables will be capable of much more.
I am guessing the 400A
fuse comment is for the DC side and not the AC side.
Now in terms of
Fuse location, the point of the
fuse being close to the source of the power is important, but take into account the
Multiplus is also a source of power so fuses are relevant at both ends. The
Multiplus will have an internal DC
fuse so you would not want/need to add an
fuse inside the box (and there would not be room anyway).
If your DC cable run was quite long, or you were running a cable through a metal panel, you might want to fit a
fuse on the
Multiplus side of the cable as well as the
battery side as a precaution. But it is always a good idea to make that DC cable from
Multiplus to
Battery as short as you can anyway.
You are using 35mm2 cable with the intention of changing to 70mm2 later on? If you have a look at the connections inside the
Multiplus 12/3000/120, you will see there are 2 big bolts for -ve, and another 2 for +ve. So you could if it suits add a 2nd 35mm2 cable alongside the first one to give you the 70mm2 cable required.
Anderson plugs are very handy for installations where you need to move stuff around, connect and disconnect kit, try out different options, etc, but I don't see a real use for them in an installation where you have a permanent
battery bank connected to an installed
Multiplus. Why are you particularly looking to use Anderson Plugs at all? I'd just use straight ring terminals on the
Multiplus going to ring terminals on the
battery connections, via
Fuse Holder/Isolation Switch as appropriate (again probably with Ring terminals on those being the most common).