I think Shortcuit has a better grasp than some others.
For the record I have seen an extension cable fused together. I forgot to uncoil it when using with a 2KW heater! But on this lead was printed Max capacity unwound 2400W, wound 900W. Therefore using it wound with a mobile phone charger or even a small TV would not present a problem.
The heat generated in the cable is primarily proportional to the square of the current (I^2 x R x t). Less to do with magnetic flux or anything else. The rate the heat dissipates depends on a number of things. Temperature, wind conditions, or if the cable has a casing etc. Rated capacities of wound and unwound cables would likely take into account current or any magnetic effects under poor cooling conditions. Usually a coiled hook up cable has good cooling conditions, being external and having no cover.
Typically a wound cable would only melt outside the van and then trip your breakers. If it was in an awning and close to ignitable materials.... unlucky.
I'd agree if you've no idea what you are doing, unwind it every time. If you know what you are going to use and have full control, there is no need espec if it's external.
For the record I have seen an extension cable fused together. I forgot to uncoil it when using with a 2KW heater! But on this lead was printed Max capacity unwound 2400W, wound 900W. Therefore using it wound with a mobile phone charger or even a small TV would not present a problem.
The heat generated in the cable is primarily proportional to the square of the current (I^2 x R x t). Less to do with magnetic flux or anything else. The rate the heat dissipates depends on a number of things. Temperature, wind conditions, or if the cable has a casing etc. Rated capacities of wound and unwound cables would likely take into account current or any magnetic effects under poor cooling conditions. Usually a coiled hook up cable has good cooling conditions, being external and having no cover.
Typically a wound cable would only melt outside the van and then trip your breakers. If it was in an awning and close to ignitable materials.... unlucky.
I'd agree if you've no idea what you are doing, unwind it every time. If you know what you are going to use and have full control, there is no need espec if it's external.