If you scroll down to the materials and care section of the Amazon listing it says that the contact material is aluminium so it may not even be copperThe copper core needs to be at least 2mm in diameter to carry 15A.
An aluminium switch contact wouldn't last long! Probably the cable? Probably something else that's aluminium? You never know these days with online descriptions. This along with the fact that the cables are pretty thin and according to some reviews aren't particularly well crimped anyway would suggest a decent choice would be to rewire the inputs at least.If you scroll down to the materials and care section of the Amazon listing it says that the contact material is aluminium so it may not even be copper
View attachment 207116
Regards,
Del
It changes all of the current carrying capacity calculations because copper will carry about 35% more current than Ali of the same CSA.Is aluminium rather than copper a problem?
Thanks so much. I have taken up so much life your time but you have been so helpful as you have previously.It changes all of the current carrying capacity calculations because copper will carry about 35% more current than Ali of the same CSA.
Ultimately we're only guessing at the cable sizes anyway but based on what's been guessed at and said previously you'd change those 5A fuses for 3A. I can't recall your list of intended loads but 3A is still likely to be ok for you.
So that's about 1.3mm². Good for about 6.5A if it's copper.P.S. The wiring on the control panel is
16 AWG.
Hello MerlSo that's about 1.3mm². Good for about 6.5A if it's copper.