Scenario:
I have a 10A 12v load which requires a 4m long cable, 1.0mm² will suffice (fused 10A). To ensure minimal volt drop I choose, say, a 10mm² cable and because the cable ends will now not fit in the terminations I would fit bootlace ferrules or wire pin crimps. Now if not available, I could cut the end conductors down to say 4.0mm², this would still be 4 x larger than the original cable, and whilst the overall current carrying capacity of the cable is reduced it is still greater than the design current of the circuit.
So whilst it may not be the correct way to terminate the cable it can be done without reducing the current carrying capacity below the design current of the circuit.
Please do not confuse capacity with load. I made a simple statement that does not change, "Cutting cores reduces the current carrying capacity of the cable" I make this statement in order that it is understood that if you use a suitable length of cable to carry the load you require which may be near the cables maximum current carrying capacity you cannot cut cores off just to make it fit a terminal